I just hooked up my PC after my move and when I try and turn it on it beeps once (I think) and then I trip the breaker. Anyone have any ideas what this could be? Power supply? I can post more info if it is required.

Thanks in advance.
Boblobla is offline   Reply With Quote
Old 06-25-2009, 06:51 PM   #2
Galakanokis
#1 Goaltender
 
Galakanokis's Avatar
 
Join Date: Apr 2006
Location: Sadly not in the Dome.
Exp:
Default

Have you reseated the cards and connectors inside already?
Galakanokis is offline   Reply With Quote
Old 06-25-2009, 06:57 PM   #3
Boblobla
Franchise Player
 
Boblobla's Avatar
 
Join Date: Apr 2008
Location: Calgary
Exp:
Default

no, does reaseated mean make sure they are properly hooked up?

and it isn't one beep, it is a double beep twice
Boblobla is offline   Reply With Quote
Old 06-25-2009, 07:04 PM   #4
Bobblehead
Franchise Player
 
Bobblehead's Avatar
 
Join Date: Jul 2005
Location: in your blind spot.
Exp:
Default

Something has shaken loose.

You'll need to open it up and make sure the cards are all firmly in their slots and all the cables are still hooked up correctly.

The beeps you hear are part of the Power On Self Test (POST) just letting you know something isn't right. Some motherboards give a specific sequence of beeps depending upon the problem, others have a few LEDs. But there is no standard and you need the motherboard manual to know what the beeps mean.

But since you just moved, a card or connection is probably loose.
__________________
"The problem with any ideology is that it gives the answer before you look at the evidence."
—Bill Clinton
"The greatest obstacle to discovery is not ignorance--it is the illusion of knowledge."
—Daniel J. Boorstin, historian, former Librarian of Congress
"But the Senator, while insisting he was not intoxicated, could not explain his nudity"
—WKRP in Cincinatti
Bobblehead is offline   Reply With Quote
The Following User Says Thank You to Bobblehead For This Useful Post:
Old 06-25-2009, 07:06 PM   #5
ricosuave
Threadkiller
 
ricosuave's Avatar
 
Join Date: Oct 2003
Location: 51.0544° N, 114.0669° W
Exp:
Default

also try powering the comp from a different outlet
__________________
https://www.reddit.com/r/CalgaryFlames/
I’m always amazed these sportscasters and announcers can call the game with McDavid’s **** in their mouths all the time.
ricosuave is offline   Reply With Quote
Old 06-25-2009, 07:21 PM   #6
Boblobla
Franchise Player
 
Boblobla's Avatar
 
Join Date: Apr 2008
Location: Calgary
Exp:
Default

A loose connection will blow a breaker?
Boblobla is offline   Reply With Quote
Old 06-25-2009, 07:24 PM   #7
sclitheroe
#1 Goaltender
 
Join Date: Sep 2005
Exp:
Default

Quote:
Originally Posted by Boblobla View Post
A loose connection will blow a breaker?
If its an outlet in a bedroom, on a fairly recent home, it will have a spark detect breaker that can trip from loose or dodgy connections. They don't necessarily trip right away like a GFI either.

But the POST beeps also indicate a problem, unrelated to the outlet, to be sure.
__________________
-Scott
sclitheroe is offline   Reply With Quote
Old 06-25-2009, 07:29 PM   #8
Boblobla
Franchise Player
 
Boblobla's Avatar
 
Join Date: Apr 2008
Location: Calgary
Exp:
Default

Alright, my problem just got a lot more expensive I think...

The computer starts up, with no beeps, in the bathroom. I have discovered that all 3 upstairs bedrooms are on the same breaker. I unplugged everything other than my PC and it still tripped the breaker.
Boblobla is offline   Reply With Quote
Old 06-25-2009, 07:37 PM   #9
ricosuave
Threadkiller
 
ricosuave's Avatar
 
Join Date: Oct 2003
Location: 51.0544° N, 114.0669° W
Exp:
Default

sounds like youve got to open up the comp and check it out
__________________
https://www.reddit.com/r/CalgaryFlames/
I’m always amazed these sportscasters and announcers can call the game with McDavid’s **** in their mouths all the time.

Last edited by ricosuave; 06-25-2009 at 07:58 PM.
ricosuave is offline   Reply With Quote
Old 06-25-2009, 07:47 PM   #10
Cliche
Powerplay Quarterback
 
Cliche's Avatar
 
Join Date: Apr 2006
Location: Wherever you go there you are.
Exp:
Default

Could be the power supply is your problem. When I last replaced the PSU, all the magic smoke came out of the capicitors in the PSU. Also check for shorted circuits, IE:molex contacting the metal frame of the comp.
__________________
Tacitus: Rara temporum felicitate, ubi sentire quae velis, et quae sentias dicere licet.
Cliche is offline   Reply With Quote
Old 06-26-2009, 10:29 AM   #11
Raekwon
First Line Centre
 
Raekwon's Avatar
 
Join Date: Nov 2007
Location: Airdrie, Alberta
Exp:
Default

Pulled off a website regarding the sensitivity of arc fault breakers.

"It could well be the heat, and the Arc Fault module

may have little to do with your problem.

Breakers in general operate on thermal/magnetic

trip sensors, (the Arc Fault sensor is designed to

recognize a high resistance arcing fault such as

those commonly associated with extention cord fires

by its electronic 'signature').

The thermal portion of the trip sensor is for overloads.

If that panel is being externally heated, the breakers may

well trip at lower than rated currents.

I'd suggest shading that panel.

Don't restrict air circulation though."


This is a complete guess but try running the computer through a UPS.
Raekwon is offline   Reply With Quote
Old 06-27-2009, 09:11 PM   #12
sclitheroe
#1 Goaltender
 
Join Date: Sep 2005
Exp:
Default

Quote:
Originally Posted by Raekwon View Post
Pulled off a website regarding the sensitivity of arc fault breakers.

"It could well be the heat, and the Arc Fault module

may have little to do with your problem.

Breakers in general operate on thermal/magnetic

trip sensors, (the Arc Fault sensor is designed to

recognize a high resistance arcing fault such as

those commonly associated with extention cord fires

by its electronic 'signature').

The thermal portion of the trip sensor is for overloads.

If that panel is being externally heated, the breakers may

well trip at lower than rated currents.

I'd suggest shading that panel.

Don't restrict air circulation though."


This is a complete guess but try running the computer through a UPS.
In my experience with the arc fault breakers and the laser printer I had that would trip it, an electrician showed me a trick. It can actually happen because the hot wire is too close to the grounded receptacle box (I believe that was his explanation). He shut the breaker off, pulled the receptacle out of the box, neatly fed the wires back in, and the problem was solved. Someone with more electrical background than me can probably explain why that happens, but in my case, simply removing (not disconnecting) the plug and then neatly reinstalling it in the receptacle box was all it took, and the circuit on that breaker has been flawless ever since.

Also - the bathroom outlet is a GFI, so if in fact there was a ground fault (short circuit) in your PC at the power supply level, the GFI would have tripped right away. If the machine POSTS (gets to the BIOS screen) without beeps in the bathroom, there's probably nothing wrong with the PC.
__________________
-Scott

Last edited by sclitheroe; 06-27-2009 at 09:13 PM. Reason: gfi
sclitheroe is offline   Reply With Quote
The Following User Says Thank You to sclitheroe For This Useful Post:
Old 06-28-2009, 12:25 PM   #13
Boblobla
Franchise Player
 
Boblobla's Avatar
 
Join Date: Apr 2008
Location: Calgary
Exp:
Default

It was my fans that were tripping the breaker. I swapped the breaker and everything is working fine.
Boblobla is offline   Reply With Quote
Old 06-28-2009, 07:08 PM   #14
Bobblehead
Franchise Player
 
Bobblehead's Avatar
 
Join Date: Jul 2005
Location: in your blind spot.
Exp:
Default

Quote:
Originally Posted by Boblobla View Post
It was my fans that were tripping the breaker. I swapped the breaker and everything is working fine.
Does it look like this?

__________________
"The problem with any ideology is that it gives the answer before you look at the evidence."
—Bill Clinton
"The greatest obstacle to discovery is not ignorance--it is the illusion of knowledge."
—Daniel J. Boorstin, historian, former Librarian of Congress
"But the Senator, while insisting he was not intoxicated, could not explain his nudity"
—WKRP in Cincinatti
Bobblehead is offline   Reply With Quote
The Following User Says Thank You to Bobblehead For This Useful Post:
Old 06-29-2009, 09:16 AM   #15
Boblobla
Franchise Player
 
Boblobla's Avatar
 
Join Date: Apr 2008
Location: Calgary
Exp:
Default

HA, it does not, but I do have about 8 fans running in my case. The electrician I talked to said it is the way some of the windings in the fan are done and it creates what appears to the breaker as a brief short circuit.
Boblobla is offline   Reply With Quote
Old 06-29-2009, 09:58 AM   #16
Bobblehead
Franchise Player
 
Bobblehead's Avatar
 
Join Date: Jul 2005
Location: in your blind spot.
Exp:
Default

Quote:
Originally Posted by Boblobla View Post
HA, it does not, but I do have about 8 fans running in my case. The electrician I talked to said it is the way some of the windings in the fan are done and it creates what appears to the breaker as a brief short circuit.
8? So it is more a system like this one:

__________________
"The problem with any ideology is that it gives the answer before you look at the evidence."
—Bill Clinton
"The greatest obstacle to discovery is not ignorance--it is the illusion of knowledge."
—Daniel J. Boorstin, historian, former Librarian of Congress
"But the Senator, while insisting he was not intoxicated, could not explain his nudity"
—WKRP in Cincinatti
Bobblehead is offline   Reply With Quote
The Following User Says Thank You to Bobblehead For This Useful Post:
Reply

Tags
man i am a n00b


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -6. The time now is 08:15 AM.

Calgary Flames
2024-25




Powered by vBulletin® Version 3.8.4
Copyright ©2000 - 2025, Jelsoft Enterprises Ltd.
Copyright Calgarypuck 2021 | See Our Privacy Policy