Quote:
Originally Posted by Wormius View Post
Wouldn’t they take up more space than a marrette though? I guess I’d have to see them side-by-side. I could see it getting crowded in some busier junction boxes.
Speaking only from what I've read other people say and not from experience, but they seem to generally take up less space in a box due to their ability to lie flat and they make it easier to arrange the wires in the box for a better fit.

Quote:
Originally Posted by PaperBagger'14 View Post
No professional should use them. Are they passable for a homeowner who doesn't know any better? Yes, but I would never put them in my house
What specifically is wrong with them? I've never used them myself, genuinely curious. I saw some people using them on YouTube and was intrigued.
Aegypticus is offline   Reply With Quote
Old 11-11-2021, 10:28 AM   #4282
PaperBagger'14
Franchise Player
 
PaperBagger'14's Avatar
 
Join Date: Apr 2013
Location: Cowtown
Exp:
Default

Quote:
Originally Posted by Aegypticus View Post
Speaking only from what I've read other people say and not from experience, but they seem to generally take up less space in a box due to their ability to lie flat and they make it easier to arrange the wires in the box for a better fit.



What specifically is wrong with them? I've never used them myself, genuinely curious. I saw some people using them on YouTube and was intrigued.
Compared to a regular splice the connection is very poor, they aren't compatible with aluminum wiring and those plastic clips you push down can break. Using them is similar to back stabbing a plug (when you don't wrap the wires around the screws but instead push them in the holes in the back of the plug), it greatly increases the chance of having an open circuit in the future.
__________________
Quote:
Originally Posted by oilboimcdavid View Post
Eakins wasn't a bad coach, the team just had 2 bad years, they should've been more patient.
PaperBagger'14 is offline   Reply With Quote
The Following User Says Thank You to PaperBagger'14 For This Useful Post:
Old 11-11-2021, 10:33 AM   #4283
Fuzz
Franchise Player
 
Fuzz's Avatar
 
Join Date: Mar 2015
Exp:
Default

I find it crazy that every electrician I have ever talked to says don't use the backstab, yet they are on almost every device. If they are so bad, why even have them? I've never used them, personally, because I listen to my sparkies. Just curious.
Fuzz is online now   Reply With Quote
Old 11-11-2021, 12:30 PM   #4284
timun
First Line Centre
 
Join Date: May 2012
Exp:
Default

Quote:
Originally Posted by PaperBagger'14 View Post
Compared to a regular splice the connection is very poor,
I find that incredibly hard to believe...

Quote:
they aren't compatible with aluminum wiring
That's a false dichotomy; wire nuts aren't compatible with aluminum wiring either.
timun is offline   Reply With Quote
Old 11-11-2021, 12:38 PM   #4285
Wormius
Franchise Player
 
Wormius's Avatar
 
Join Date: Feb 2011
Location: Somewhere down the crazy river.
Exp:
Default

The backstabs are a pain in the arse to remove. I have had varying degrees of success and all involved some amount of intent.
Wormius is offline   Reply With Quote
Old 11-11-2021, 01:33 PM   #4286
PaperBagger'14
Franchise Player
 
PaperBagger'14's Avatar
 
Join Date: Apr 2013
Location: Cowtown
Exp:
Default

Quote:
Originally Posted by timun View Post
I find that incredibly hard to believe...



That's a false dichotomy; wire nuts aren't compatible with aluminum wiring either.
A quick contact resistance test would prove you wrong, it's actually very easy to prove with a ductor and about 10 seconds of time. Also a little research would show that there are in fact marrettes for aluminum wiring, you can even find them at specialty electrical stores like home depot.

https://www.homedepot.ca/product/mar...ck-/1000148262
__________________
Quote:
Originally Posted by oilboimcdavid View Post
Eakins wasn't a bad coach, the team just had 2 bad years, they should've been more patient.
PaperBagger'14 is offline   Reply With Quote
Old 11-11-2021, 01:51 PM   #4287
timun
First Line Centre
 
Join Date: May 2012
Exp:
Default

Quote:
Originally Posted by PaperBagger'14 View Post
Also a little research would show that there are in fact marrettes for aluminum wiring, you can even find them at specialty electrical stores like home depot.

https://www.homedepot.ca/product/mar...ck-/1000148262
Okay, I stand corrected. I've only ever seen the purple Al-to-Cu ones. I'll freely admit this limitation is completely irrelevant to me as I have no aluminum wiring in my house, but it stands to reason a professional has to deal with Al-to-Al sometimes.

Quote:
A quick contact resistance test would prove you wrong, it's actually very easy to prove with a ductor and about 10 seconds of time.
I thought you meant that the mechanical connection is worse. From the youtube videos I've watched of people using them they're very snug and resist a tug test better than a wire nut.

With respect to the electrical connection, I would imagine they have a slightly higher resistance because the conductors are not in direct contact, but I find it incredulous that it'll make much of a difference. At least, on typical 120 VAC/15 A circuits the likes you'd find in a house.
timun is offline   Reply With Quote
Old 11-11-2021, 02:16 PM   #4288
PaperBagger'14
Franchise Player
 
PaperBagger'14's Avatar
 
Join Date: Apr 2013
Location: Cowtown
Exp:
Default

Quote:
Originally Posted by timun View Post
Okay, I stand corrected. I've only ever seen the purple Al-to-Cu ones. I'll freely admit this limitation is completely irrelevant to me as I have no aluminum wiring in my house, but it stands to reason a professional has to deal with Al-to-Al sometimes.



I thought you meant that the mechanical connection is worse. From the youtube videos I've watched of people using them they're very snug and resist a tug test better than a wire nut.

With respect to the electrical connection, I would imagine they have a slightly higher resistance because the conductors are not in direct contact, but I find it incredulous that it'll make much of a difference. At least, on typical 120 VAC/15 A circuits the likes you'd find in a house.
The tensile strength of each type has its limitations, if you're using wagos to connect to a load with a modest amount of current flowing as well as vibration (aka a small transformer) they operate worse mechanically than a wire nut. Tug test they are probably better but that isn't very relevant as you'll never be tugging on a wire once it's installed.

The difference is huge in electrical connection. Take this video for example:



In this video, he uses only 1A of current for the test (he should be using closer to 20A to actually stress the connection for a useful result). Long story short he gets 6.8 mOhm of resistance at 1A for the wago and 6.5mOhm for a wire nut.

Those are useful to know, but had he used 20A and measured watts lost (aka heat generated) from the connection using the formula P=I^2 X R.

P=20^2 x 6.8 = 2.720W lost from the wago + wire
P=20^2 x 6.5 = 2.600W lost from the wire nut + wire

This equates to a 5% increase in heat generated by a wago. Heat related failure is also not linear when it comes to equipment lifespan, its actually exponential so a 5% difference is substantial.

Of note, he didn't strip back enough on the wire nut to meet the manufacturers spec. He also didn't pre twist the wires which is a manufacturer spec but is not consistent with best trade practices. The value of 6.5mOhm could be dropped even further with having a larger contact area and pre twisting the wires.

This is all napkin math and there will be some rounding errors here, but for all intents and purposes it demonstrates my point.
__________________
Quote:
Originally Posted by oilboimcdavid View Post
Eakins wasn't a bad coach, the team just had 2 bad years, they should've been more patient.

Last edited by PaperBagger'14; 11-11-2021 at 02:19 PM.
PaperBagger'14 is offline   Reply With Quote
The Following User Says Thank You to PaperBagger'14 For This Useful Post:
Old 11-11-2021, 02:19 PM   #4289
Fuzz
Franchise Player
 
Fuzz's Avatar
 
Join Date: Mar 2015
Exp:
Default


At about 1 minute in, you can see the lever action. The electrical contact area is actually pretty small. I could see how that's not ideal.
Fuzz is online now   Reply With Quote
The Following User Says Thank You to Fuzz For This Useful Post:
Old 11-11-2021, 02:22 PM   #4290
Fuzz
Franchise Player
 
Fuzz's Avatar
 
Join Date: Mar 2015
Exp:
Default

Quote:
Originally Posted by PaperBagger'14 View Post
The tensile strength of each type has its limitations, if you're using wagos to connect to a load with a modest amount of current flowing as well as vibration (aka a small transformer) they operate worse mechanically than a wire nut. Tug test they are probably better but that isn't very relevant as you'll never be tugging on a wire once it's installed.

The difference is huge in electrical connection. Take this video for example:


In this video, he uses only 1A of current for the test (he should be using closer to 20A to actually stress the connection for a useful result). Long story short he gets 6.8 mOhm of resistance at 1A for the wago and 6.5mOhm for a wire nut.

Those are useful to know, but had he used 20A and measured watts lost (aka heat generated) from the connection using the formula P=I^2 X R.

P=20^2 x 6.8 = 2.720W lost from the wago + wire
P=20^2 x 6.5 = 2.600W lost from the wire nut + wire

This equates to a 5% increase in heat generated by a wago. Heat related failure is also not linear when it comes to equipment lifespan, its actually exponential so a 5% difference is substantial.

Of note, he didn't strip back enough on the wire nut to meet the manufacturers spec. He also didn't pre twist the wires which is a manufacturer spec but is not consistent with best trade practices. The value of 6.5mOhm could be dropped even further with having a larger contact area and pre twisting the wires.

This is all napkin math and there will be some rounding errors here, but for all intents and purposes it demonstrates my point.
Could you clarify...is pre-twisting best practice, or not? I've always per-twisted, I'm just confused by your wording.
Fuzz is online now   Reply With Quote
Old 11-11-2021, 02:30 PM   #4291
PaperBagger'14
Franchise Player
 
PaperBagger'14's Avatar
 
Join Date: Apr 2013
Location: Cowtown
Exp:
Default

Quote:
Originally Posted by Fuzz View Post
Could you clarify...is pre-twisting best practice, or not? I've always per-twisted, I'm just confused by your wording.
Always pre twist, pre twisting is the best practice especially with stranded conductors which may get frayed inside the wire nut and not make contact.
__________________
Quote:
Originally Posted by oilboimcdavid View Post
Eakins wasn't a bad coach, the team just had 2 bad years, they should've been more patient.
PaperBagger'14 is offline   Reply With Quote
The Following User Says Thank You to PaperBagger'14 For This Useful Post:
Old 11-11-2021, 02:36 PM   #4292
CroFlames
Franchise Player
 
CroFlames's Avatar
 
Join Date: Feb 2015
Exp:
Default

Quote:
Originally Posted by PaperBagger'14 View Post
The tensile strength of each type has its limitations, if you're using wagos to connect to a load with a modest amount of current flowing as well as vibration (aka a small transformer) they operate worse mechanically than a wire nut. Tug test they are probably better but that isn't very relevant as you'll never be tugging on a wire once it's installed.

The difference is huge in electrical connection. Take this video for example:



In this video, he uses only 1A of current for the test (he should be using closer to 20A to actually stress the connection for a useful result). Long story short he gets 6.8 mOhm of resistance at 1A for the wago and 6.5mOhm for a wire nut.

Those are useful to know, but had he used 20A and measured watts lost (aka heat generated) from the connection using the formula P=I^2 X R.

P=20^2 x 6.8 = 2.720W lost from the wago + wire
P=20^2 x 6.5 = 2.600W lost from the wire nut + wire

This equates to a 5% increase in heat generated by a wago. Heat related failure is also not linear when it comes to equipment lifespan, its actually exponential so a 5% difference is substantial.

Of note, he didn't strip back enough on the wire nut to meet the manufacturers spec. He also didn't pre twist the wires which is a manufacturer spec but is not consistent with best trade practices. The value of 6.5mOhm could be dropped even further with having a larger contact area and pre twisting the wires.

This is all napkin math and there will be some rounding errors here, but for all intents and purposes it demonstrates my point.

I was told there would be no formulas on the exam.
CroFlames is offline   Reply With Quote
Old 11-11-2021, 02:47 PM   #4293
opendoor
Franchise Player
 
Join Date: Apr 2007
Exp:
Default

They use Wago type connectors a lot in Europe. I wonder if having 240V combined with using 2.5mm wire (slightly thicker than 14 AWG) for most plug circuits means less current/heat generally? Of course they also use ring circuits in the UK which sounds like an absolutely terrible idea to me in terms of safety.
opendoor is offline   Reply With Quote
Old 11-11-2021, 07:50 PM   #4294
I_H8_Crawford
Franchise Player
 
I_H8_Crawford's Avatar
 
Join Date: Apr 2004
Location: Calgary
Exp:
Default

So finally getting around to working on my doorbell which isnt working, discovered that the live wire from the transformer to the breaker box is disconnected. Ground wire still connected.

I remember the home inspector showing how it was double tapped on another breaker and saying that is the only time you can double tap - my question - do I need an electrician to attach it again, or am I good to attach it to one of the 15 amp breakers? OR am I better off just getting another breaker for it.
I_H8_Crawford is offline   Reply With Quote
Old 11-11-2021, 08:21 PM   #4295
PaperBagger'14
Franchise Player
 
PaperBagger'14's Avatar
 
Join Date: Apr 2013
Location: Cowtown
Exp:
Default

Quote:
Originally Posted by I_H8_Crawford View Post
So finally getting around to working on my doorbell which isnt working, discovered that the live wire from the transformer to the breaker box is disconnected. Ground wire still connected.

I remember the home inspector showing how it was double tapped on another breaker and saying that is the only time you can double tap - my question - do I need an electrician to attach it again, or am I good to attach it to one of the 15 amp breakers? OR am I better off just getting another breaker for it.
Shut the breaker off, check the end of the wire that was in the breaker for damage. If it doesn't look burnt put it back in and tighten it down and turn the breaker on.
__________________
Quote:
Originally Posted by oilboimcdavid View Post
Eakins wasn't a bad coach, the team just had 2 bad years, they should've been more patient.
PaperBagger'14 is offline   Reply With Quote
Old 11-11-2021, 10:19 PM   #4296
DropIt
Franchise Player
 
DropIt's Avatar
 
Join Date: Sep 2009
Location: Red Deer, AB
Exp:
Default

Quote:
Originally Posted by I_H8_Crawford View Post
So finally getting around to working on my doorbell which isnt working, discovered that the live wire from the transformer to the breaker box is disconnected. Ground wire still connected.

I remember the home inspector showing how it was double tapped on another breaker and saying that is the only time you can double tap - my question - do I need an electrician to attach it again, or am I good to attach it to one of the 15 amp breakers? OR am I better off just getting another breaker for it.
I've also seen many people tie it into their panel plug instead to avoid rooting around through a crowded panel.
DropIt is offline   Reply With Quote
Old 11-13-2021, 09:51 AM   #4297
81MC
#1 Goaltender
 
Join Date: Aug 2017
Exp:
Default

Anyone use a thermostatic plug-in outlet, similar to https://www.amazon.com/DIGITEN-Wirel...ROL_THERMOSTAT?

I have one of those electric ‘fireplace’ units with a dedicated circuit, but the unit itself is either on or off. I’d like to change the switch to a thermostat like you see on most space heaters, but an outlet control might be okay.
__________________
No, no…I’m not sloppy, or lazy. This is a sign of the boredom.
81MC is offline   Reply With Quote
Old 11-13-2021, 11:11 AM   #4298
timun
First Line Centre
 
Join Date: May 2012
Exp:
Default

Quote:
Originally Posted by PaperBagger'14 View Post
The tensile strength of each type has its limitations, if you're using wagos to connect to a load with a <...clipped for brevity...>
If anything that video proves that the difference between wire nuts and wagos is actually pretty much insignificant. Certainly not definitive; there's more variability in resistance due to how the alligator clips were making contact with the other ends of the wires.

Taking your back-of-the-napkin calculations further, a 20 A load on a 120 V circuit draws 2400 W, so the difference between a wire nut and a wago is

[(2402.72 / 2402.6) - 1] * 100 = 0.005%

Respectfully: whoop-de-####ing-do.
timun is offline   Reply With Quote
Old 11-13-2021, 06:19 PM   #4299
jwslam
Scoring Winger
 
Join Date: Jul 2014
Exp:
Default

played locksmith today
jwslam is offline   Reply With Quote
Old 11-14-2021, 12:33 AM   #4300
DoubleF
Franchise Player
 
DoubleF's Avatar
 
Join Date: Apr 2014
Exp:
Default

Quote:
Originally Posted by jwslam View Post
played locksmith today
I thought the Weiser smart key system seemed easier to use than the stuff in this video. I redid my house myself with them when I took possession of my place.
DoubleF is offline   Reply With Quote
The Following User Says Thank You to DoubleF For This Useful Post:
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -6. The time now is 04:52 PM.

Calgary Flames
2023-24




Powered by vBulletin® Version 3.8.4
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright Calgarypuck 2021