Default Who could fix this?

I'm reaching out for CP wisdom as I'm not sure how to go about repairing this.

When we started using our master bathroom a water stain started appearing between the exhaust fan and the wall. (Other side of the wall is the exterior/siding). The stain has been growing over the past few years and I can't tell if it has slowed since we've installed a 60 minute fan timer to get rid of the moisture and humidity after showers.

The house was built about 4 years ago however the stain started appearing 3 years ago when we started using the bathroom on a regular basis. Who would I call to get this repaired? A roofing company doesn't seem right because it is inside the house, but a HVAC company doesn't seem right either since it is a stain/leak on the inside of the house and not furnace related. With this in mind, I'm not sure if the leak is coming from the outside of the house in, or the other way around.

Help?

p.s. here is a bad picture of what I'm talking about.
http://www.flickr.com/photos/27856280@N02/6208535344/
Bean is offline   Reply With Quote
Old 10-03-2011, 12:38 PM   #2
Ashartus
First Line Centre
 
Join Date: Mar 2007
Location: Calgary
Exp:
Default

Is your new home warranty still valid? If so I suggest contacting the builder first.
Ashartus is offline   Reply With Quote
Old 10-03-2011, 12:47 PM   #3
Bean
Scoring Winger
 
Join Date: May 2004
Exp:
Default

Our warranty through the builder has expired for a while now. Alberta New Home Warranty might be an option but only if this is considered a 'structural' problem.

I'm not sure if the leak would come from the attic but in my opinion; that'd be tough for me to prove as structural without a second opinion.
Bean is offline   Reply With Quote
Old 10-03-2011, 12:52 PM   #4
Sliver
evil of fart
 
Sliver's Avatar
 
Join Date: Sep 2009
Exp:
Default

Could be condensation on your exhaust ducting (warm air from your bathroom hits cold air in the attic). The ducting should be insulated (if it's not, I'd start there) and there should be a bend in the ducting that will allow water to collect and evaporate on the inside of the ducting versus just dripping down onto your ceiling.

As for who you'd call - I paid an electrician to install a new fan in my bathroom and he added the insulated ducting while he was up there.
Sliver is offline   Reply With Quote
The Following User Says Thank You to Sliver For This Useful Post:
Old 10-03-2011, 12:56 PM   #5
Delthefunky
First Line Centre
 
Delthefunky's Avatar
 
Join Date: Sep 2004
Location: Vernon, BC
Exp:
Default

I assume there is an attic or crawl space above the washroom? If so, I would try and take a peak up there just to see if there is any evidence of where the moisture is coming from. Could be the roof.

Otherwise I would say it's coming from moisture in the washroom. Maybe the ceiling fan helps maybe not.

A quick fix if you don't think there is much or any water damage would be just to paint it. If your concerned about mold you can get a remediation spray. Otherwise, phone a handy-man!
Delthefunky is offline   Reply With Quote
Old 10-03-2011, 01:08 PM   #6
topfiverecords
Franchise Player
 
topfiverecords's Avatar
 
Join Date: Feb 2010
Location: Park Hyatt Tokyo
Exp:
Default

Sounds like condensation is forming on the vent pipe in the attic and then dripping back down onto the ceiling.
topfiverecords is offline   Reply With Quote
Old 10-03-2011, 01:31 PM   #7
Caged Great
Franchise Player
 
Caged Great's Avatar
 
Join Date: Oct 2006
Location: Calgary
Exp:
Default

Quote:
Originally Posted by topfiverecords View Post
Sounds like condensation is forming on the vent pipe in the attic and then dripping back down onto the ceiling.
That's what I would assume as well, otherwise it might be a leaking roof.
__________________
Fireside Chat - The #1 Flames Fan Podcast - FiresideChat.ca
Caged Great is offline   Reply With Quote
Old 10-03-2011, 01:49 PM   #8
Robotic
Scoring Winger
 
Robotic's Avatar
 
Join Date: Apr 2011
Location: AI
Exp:
Default

I'd take a look in your attic and see if there is any mold or condensation build up. Make sure when you look into your attic you can see some light coming in from outside as there needs to be sufficient air movement to compensate the temperature changes outside. If there isnt then you may have a good idea whats wrong.
Robotic is offline   Reply With Quote
Old 10-03-2011, 03:50 PM   #9
yads
Powerplay Quarterback
 
Join Date: Apr 2008
Exp:
Default

You can take a look yourself, as for who's going to fix it, get a drywall guy.
yads is offline   Reply With Quote
Old 10-03-2011, 05:18 PM   #10
Bagor
Franchise Player
 
Bagor's Avatar
 
Join Date: Jun 2008
Location: Spartanville
Exp:
Default

Quote:
Originally Posted by Sliver View Post
there should be a bend in the ducting that will allow water to collect and evaporate on the inside of the ducting versus just dripping down onto your ceiling.


It should be as straight as possible for airflow and fan performance.

Agreed that it sounds like a poorly insulated, not sealed duct pipe.
__________________


Bagor is offline   Reply With Quote
Old 10-03-2011, 08:22 PM   #11
DuffMan
Franchise Player
 
DuffMan's Avatar
 
Join Date: Apr 2004
Location: 127.0.0.1
Exp:
Default

are both those walls exterior?
You should find your attic access panel and stick your head up there with a flashlight and have a look at the piping like others mentioned.
I think it something to do with the exterior though.
__________________
Pass the bacon.
DuffMan is offline   Reply With Quote
Old 10-03-2011, 08:59 PM   #12
BEANZ
Scoring Winger
 
Join Date: Aug 2007
Exp:
Default

Quote:
Originally Posted by Bagor View Post


It should be as straight as possible for airflow and fan performance.

Agreed that it sounds like a poorly insulated, not sealed duct pipe.

You sir are incorrect. A straight exaust pipe in our climate will result in moisture dripping thru the fan on a regular basis. As Sliver stated the pipe needs to be bent to allow any condensation to collect rather than drip onto the ceiling/floor.
BEANZ is offline   Reply With Quote
Old 10-03-2011, 09:45 PM   #13
Robbob
Franchise Player
 
Join Date: Jul 2003
Exp:
Default

Shouldn't venting from exhaust fans all be one peice insulated flex? If it were hard pipe I would be concerned unless it is part of some air make up system.
Robbob is offline   Reply With Quote
Old 10-03-2011, 09:52 PM   #14
DuffMan
Franchise Player
 
DuffMan's Avatar
 
Join Date: Apr 2004
Location: 127.0.0.1
Exp:
Default

flex as in that accordian type stuff. You don't want that, or the condensation will just get caught in the ridges.

Like to know more about this bent concept though for pooling.
__________________
Pass the bacon.
DuffMan is offline   Reply With Quote
Old 10-03-2011, 10:04 PM   #15
Clarkey
Lifetime Suspension
 
Clarkey's Avatar
 
Join Date: Oct 2002
Exp:
Default

I believe your roof is leaking where the vent pipe meets the roof. Water has travelled down the side of the pipe and settled in the low spot at the edge of your wall. Get a ladder and a trouble light/flash light and crawl up into your attick and check. Make sure to only step on the beams.
Clarkey is offline   Reply With Quote
Old 10-03-2011, 10:42 PM   #16
Bagor
Franchise Player
 
Bagor's Avatar
 
Join Date: Jun 2008
Location: Spartanville
Exp:
Default

Quote:
Originally Posted by BEANZ View Post
You sir are incorrect. A straight exaust pipe in our climate will result in moisture dripping thru the fan on a regular basis. As Sliver stated the pipe needs to be bent to allow any condensation to collect rather than drip onto the ceiling/floor.
I said as straight as possible.

This is taking into account that you have to run a bend (from a 90 to a gradual) off the exhaust port of the fan itself at some stage if you're going through the roof.

If for whatever reason you're going through the side of the house why on earth would you want to create a bend (p trap) to collect water. Surely over the course of the winter you're going to have build up and resisted air flow or even completely restrict it.

Any fan manufacturer suggests as short and straight as possible.

I have never ever heard of this water collection bend. Seriously, I'd appreciate a few links.
__________________


Bagor is offline   Reply With Quote
Old 10-03-2011, 11:07 PM   #17
Jedi Ninja
Scoring Winger
 
Jedi Ninja's Avatar
 
Join Date: Mar 2009
Exp:
Default

Spray/spritz it down with a strong bleach formula. Protect clothing and towels from any overspray. Wipe any overspray off of the wall as well. Let it dry. It may take a couple of treatments. You should be able to get rid of most of the stain that way. Then watch for recurrence and note any pattern. On warm breaks in the winter, you may want to touch-test the area to see if it is moist (the stain takes a while to develop after the actual moisture gets in.) Same with heavy rains in the spring/summer.

Last edited by Jedi Ninja; 10-03-2011 at 11:10 PM.
Jedi Ninja is offline   Reply With Quote
Old 10-04-2011, 02:51 PM   #18
Bindair Dundat
Scoring Winger
 
Join Date: Feb 2010
Location: St. Albert
Exp:
Default

Quote:
Originally Posted by Bagor View Post
I said as straight as possible.

This is taking into account that you have to run a bend (from a 90 to a gradual) off the exhaust port of the fan itself at some stage if you're going through the roof.

If for whatever reason you're going through the side of the house why on earth would you want to create a bend (p trap) to collect water. Surely over the course of the winter you're going to have build up and resisted air flow or even completely restrict it.

Any fan manufacturer suggests as short and straight as possible.


I have never ever heard of this water collection bend. Seriously, I'd appreciate a few links.
I would too...

I've been R & R ing ventiliation devices for 20 odd years and this "trap" malarkey is simply not correct. Insulate them properly and allow for the best possible airflow rate through the ridgid pipe (flex is crapola).

If this is done, there will be no condensation...period.

Or maybe 20 years worth of customers are all concurrently taking pity on me, when water drips from their fans in the winter?

I have never had a call back WRT this issue.

BTW? I insulate all the ventilation ducting I install myself, wrapping it in 6 mil poly (on the warm side, i.e. tight to the pipe itself), then wrapping R-12 batt insulation around that, secured with baling wire. The "premade" crap they sell (while "technically" meeting code), is NFG for our climate...I mean the vapor barrier is on the wrong freaking side...just for starters.

Do it right, do it once.

Nuff Said.

To the OP: "Who could fix this?"

I could...but I'm up in St. Albert, and I don't think you'd much like my quote...lol!

Last edited by Bindair Dundat; 10-04-2011 at 03:11 PM. Reason: Address the OP
Bindair Dundat is offline   Reply With Quote
The Following User Says Thank You to Bindair Dundat For This Useful Post:
Old 10-04-2011, 03:24 PM   #19
4X4
One of the Nine
 
Join Date: Dec 2004
Exp:
Default

I encountered a similar problem once. It turned out that the ventilation pipe from the fan to the gooseneck had gotten disconnected right on the other side of the fan, so basically, the bathroom fan was taking that warm, moist air, and simply blowing it into the attic. In the winter, it caused a bunch of ice buildup in the attic, and then during a chinook, the ice started to melt, and water started dripping from a low point.

The reason the vent duct came disconnected is unclear, but the reason it went undetected when I simply poked my head in the attic and looked around, was because the blown in insulation concealed the disconnect.

The best advice so far in this thread is to grab a good flashlight and go up in the attic and look around. Bring a dustpan or something to scoop around the insulation, and keep your feet on the trusses. You might luck out and figure out the problem by yourself, and duct tape might actually be the answer.
4X4 is offline   Reply With Quote
Old 10-04-2011, 03:53 PM   #20
Bindair Dundat
Scoring Winger
 
Join Date: Feb 2010
Location: St. Albert
Exp:
Default

Quote:
Originally Posted by 4X4 View Post
I encountered a similar problem once. It turned out that the ventilation pipe from the fan to the gooseneck had gotten disconnected right on the other side of the fan, so basically, the bathroom fan was taking that warm, moist air, and simply blowing it into the attic. In the winter, it caused a bunch of ice buildup in the attic, and then during a chinook, the ice started to melt, and water started dripping from a low point.

The reason the vent duct came disconnected is unclear, but the reason it went undetected when I simply poked my head in the attic and looked around, was because the blown in insulation concealed the disconnect.

The best advice so far in this thread is to grab a good flashlight and go up in the attic and look around. Bring a dustpan or something to scoop around the insulation, and keep your feet on the trusses. You might luck out and figure out the problem by yourself, and duct tape might actually be the answer.
This is certainly the most likely culprit...and the first thing I would look for. It should be very obvious, as the warm air will not condense until it hits the "cold side" of the loose fill (assuming it is blown in). There would likely be a hard "puck" of coagulated insulation in the area.

A duct pipe that has developed sufficient backpressure to break this joint, indicates that there might be something else going on though...Just my opinion. Perhaps an ice dam from poor insulation (or a "drip trap"...)?

Bindair Dundat is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -6. The time now is 04:37 AM.

Calgary Flames
2024-25




Powered by vBulletin® Version 3.8.4
Copyright ©2000 - 2025, Jelsoft Enterprises Ltd.
Copyright Calgarypuck 2021 | See Our Privacy Policy