Default Help Needed - Residential Electrical Problem

Hey CP!

We have a strange electrical problem in our house.

We have four light switches and three wall plugs that don't work.

We have established that the problem is not at the breaker box. The problem stretches across two breaker circuits, but some of the things on the breakers still work.

We have tested the wall plugs and they are showing ~110 volts between hot and ground, ~107 volts between neutral and ground, and only 11 volts between hot and neutral. We have used an outlet tester and it shows hot/ground reverse but I have discovered that is probably "open neutral" instead.

We have been trying to figure this problem out for several days, including asking my friend who is an electrician to look at it. However, he works mostly commercial construction/industrial and it unfortunately baffled him as well.

Any thoughts from the CP community? Is anyone here a residential electrician?

Thanks in advance for your help!
__________________

Huge thanks to Dion for the signature!
Nehkara is offline   Reply With Quote
Old 04-22-2013, 12:22 PM   #2
Jacks
Franchise Player
 
Jacks's Avatar
 
Join Date: Mar 2011
Exp:
Default

Quote:
Originally Posted by Nehkara View Post
We have tested the wall plugs and they are showing ~110 volts between hot and ground, ~107 volts between neutral and ground, and only 11 volts between hot and neutral. We have used an outlet tester and it shows hot/ground reverse but I have discovered that is probably "open neutral" instead.
That's not good. Do not plug anything into those outlets. Call an electrician. Sounds like somebody royally screwed up the wiring on those outlets. Someone needs to open those boxes, test all the wires and then put it back together properly.

Edit: It almost sounds like you have a 3 wire coming into the boxes carrying 2 hots and someone has hooked both hot wires to the outlet.

Last edited by Jacks; 04-22-2013 at 12:27 PM.
Jacks is offline   Reply With Quote
The Following User Says Thank You to Jacks For This Useful Post:
Old 04-22-2013, 12:32 PM   #3
Nehkara
Franchise Player
 
Nehkara's Avatar
 
Join Date: Aug 2003
Location: Calgary, Alberta, Canada
Exp:
Default

Quote:
Originally Posted by Jacks View Post
That's not good. Do not plug anything into those outlets. Call an electrician. Sounds like somebody royally screwed up the wiring on those outlets. Someone needs to open those boxes, test all the wires and then put it back together properly.

Edit: It almost sounds like you have a 3 wire coming into the boxes carrying 2 hots and someone has hooked both hot wires to the outlet.
Keep in mind this wiring has not been altered in probably over 40 years. Certainly not in the last 17 years we have lived here. There was also no incident that stopped these things from working, just woke up one morning and they didn't work.

My electrician friend also checked the outlets and said they were all wired correctly, despite the very odd readings. This was part of the reason he was baffled.

Don't worry though, we will be contacting a residential electrician soon.
__________________

Huge thanks to Dion for the signature!
Nehkara is offline   Reply With Quote
Old 04-22-2013, 04:19 PM   #4
GoinAllTheWay
Franchise Player
 
GoinAllTheWay's Avatar
 
Join Date: Apr 2003
Location: Not sure
Exp:
Default

edit

nm...i see your electician friend already verified they are wired correctly.

That is one screwy issue though. If you do find the culprit, please do report back. I like hearing how these end.
GoinAllTheWay is offline   Reply With Quote
The Following User Says Thank You to GoinAllTheWay For This Useful Post:
Old 04-22-2013, 04:39 PM   #5
normtwofinger
Self-Retirement
 
Join Date: Mar 2007
Exp:
Default

Do any of your 220 appliances work?

If not, seems like there is a break in one of your main supply cables coming into the house, causing you to only have 1 110 cable functioning.

We had a similar problem. It ended up being a break in one cable after the meter.
normtwofinger is offline   Reply With Quote
The Following User Says Thank You to normtwofinger For This Useful Post:
Old 04-22-2013, 07:12 PM   #6
Nehkara
Franchise Player
 
Nehkara's Avatar
 
Join Date: Aug 2003
Location: Calgary, Alberta, Canada
Exp:
Default

Quote:
Originally Posted by normtwofinger View Post
Do any of your 220 appliances work?

If not, seems like there is a break in one of your main supply cables coming into the house, causing you to only have 1 110 cable functioning.

We had a similar problem. It ended up being a break in one cable after the meter.
Yeah all of the 220 appliances work fine.
__________________

Huge thanks to Dion for the signature!
Nehkara is offline   Reply With Quote
Old 04-22-2013, 07:31 PM   #7
ricosuave
Threadkiller
 
ricosuave's Avatar
 
Join Date: Oct 2003
Location: 51.0544° N, 114.0669° W
Exp:
Default

The receptacles you refer to, do they have UPSs installed on them, or on the same circuit as them?

I'm also wondering if it is a bad connection on the neutrals on those circuits, bad splice somewhere. Loose neutrals can cause strange things to happen.
__________________
https://www.reddit.com/r/CalgaryFlames/
I’m always amazed these sportscasters and announcers can call the game with McDavid’s **** in their mouths all the time.

Last edited by ricosuave; 04-22-2013 at 08:18 PM.
ricosuave is offline   Reply With Quote
Old 04-23-2013, 07:11 AM   #8
Bindair Dundat
Scoring Winger
 
Join Date: Feb 2010
Location: St. Albert
Exp:
Default

Quote:
Originally Posted by ricosuave View Post
The receptacles you refer to, do they have UPSs installed on them, or on the same circuit as them?

I'm also wondering if it is a bad connection on the neutrals on those circuits, bad splice somewhere. Loose neutrals can cause strange things to happen.
That would be my guess as well. Likely as not, one of the connectors with a number of neutrals spliced together has failed and is breaking the connection back to the buss bar at the panel. Sharing neutral paths is permissible among light and plug circuits when this is the most practical way to wire these circuits. The condition you describe leads me to believe that this is the case here. Call in a sparky; this situation is potentially catastrophic. The bad connection is probably in a multigang switchbox; this is where I would look first.
Bindair Dundat is offline   Reply With Quote
Old 04-23-2013, 07:47 AM   #9
speede5
First Line Centre
 
speede5's Avatar
 
Join Date: Sep 2009
Exp:
Default

No idea what else to suggest, but definately let us know what the outcome is.
speede5 is offline   Reply With Quote
Old 04-23-2013, 06:53 PM   #10
MG153
Farm Team Player
 
MG153's Avatar
 
Join Date: Mar 2013
Location: Calgary
Exp:
Default

aluminum or copper wiring?
MG153 is offline   Reply With Quote
Old 04-26-2013, 07:24 PM   #11
Bindair Dundat
Scoring Winger
 
Join Date: Feb 2010
Location: St. Albert
Exp:
Default

So? Any update on this?
I think I probably caught it (as described in my post upthread).

Inquiring minds want to know...
Bindair Dundat is offline   Reply With Quote
Old 04-26-2013, 08:54 PM   #12
Shnabdabber
Account Disabled at User's Request
 
Shnabdabber's Avatar
 
Join Date: Jun 2007
Exp:
Default

This situation sounds much like the classic ol loose neutral. Time to start digging!
Shnabdabber is offline   Reply With Quote
Old 05-06-2013, 11:19 AM   #13
GoinAllTheWay
Franchise Player
 
GoinAllTheWay's Avatar
 
Join Date: Apr 2003
Location: Not sure
Exp:
Default

/\/\/\

He's already stated an electrician friend has verified the wiring is fine.


Quote:
Originally Posted by Bindair Dundat View Post
So? Any update on this?
I think I probably caught it (as described in my post upthread).

Inquiring minds want to know...
X2!!! Updates plz!
GoinAllTheWay is offline   Reply With Quote
Old 05-07-2013, 10:02 AM   #14
speede5
First Line Centre
 
speede5's Avatar
 
Join Date: Sep 2009
Exp:
Default

There should be a law that any requests for help on forums include the resolution as a thread closer.

speede5 is offline   Reply With Quote
The Following User Says Thank You to speede5 For This Useful Post:
Old 05-07-2013, 10:05 AM   #15
GoinAllTheWay
Franchise Player
 
GoinAllTheWay's Avatar
 
Join Date: Apr 2003
Location: Not sure
Exp:
Default

Totally agree. We need to see this through to the end!
GoinAllTheWay is offline   Reply With Quote
Old 05-07-2013, 10:29 AM   #16
Ironhorse
Franchise Player
 
Ironhorse's Avatar
 
Join Date: Aug 2004
Location: Calgary
Exp:
Default

Maybe the OP has electrocuted themselves?
Ironhorse is offline   Reply With Quote
Old 05-07-2013, 10:31 AM   #17
GoinAllTheWay
Franchise Player
 
GoinAllTheWay's Avatar
 
Join Date: Apr 2003
Location: Not sure
Exp:
Default

I shouldn't but....lol!
GoinAllTheWay is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -6. The time now is 12:42 PM.

Calgary Flames
2024-25




Powered by vBulletin® Version 3.8.4
Copyright ©2000 - 2025, Jelsoft Enterprises Ltd.
Copyright Calgarypuck 2021 | See Our Privacy Policy