Calgarypuck Forums - The Unofficial Calgary Flames Fan Community
Old 10-28-2021, 10:16 AM   #1
MacDaddy77
First Line Centre
 
MacDaddy77's Avatar
 
Join Date: Sep 2006
Exp:
Default Garage heater venting clearance from Soffit?

Installing venting for garage heater 45,000btu Hot Dawg. Horizontal class 3
SS venting with termination T.

according to the manual I only need to be minimum 11" from exterior wall and vent cap and have 12" clearance above vent termination. I have more than enough to satisfy both these but is there a minimum I need to be out from Soffit of is 13" from exterior wall good enough?



Table 10.1 - Minimum Length Between External
Wall and Vent
Model Min. Length
Size Application A ➀
30-75 Residential & Commercial 11"
100, 125 Residential 12"
100, 125 Commercial 24"


C8. For a vent termination located under an eave, the distance
of the overhang must not exceed 24". The clearance to
combustibles above the exterior vent must be maintained
at a minimum of 12"
. Consult the National Fuel Gas Code
for additional requirements for eaves that have ventilation
openings
MacDaddy77 is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -6. The time now is 09:05 AM.

Calgary Flames
2024-25




Powered by vBulletin® Version 3.8.4
Copyright ©2000 - 2025, Jelsoft Enterprises Ltd.
Copyright Calgarypuck 2021 | See Our Privacy Policy