I did all of the network cabling years ago. It was pretty painful because I was trying to minimize the damage. It was a lot of fishing and magnets and everything. I am not sure if I can do the charger? Our panel is only 100A.
You will likely need a load management relay of some sort with your charger, so if you have an electric dryer or oven it will allow them to run over your charger. It’s not an issue because you are pairing the charger with something that has intermittent usage.

Most homes that go to a level 2 charger that have either an ac or hot tub are gonna need this solution since you won’t want to upgrade your service and there’s really no need to anyways as the load management keeps your below the limit of the panel.