I emailed the city and got this reply:

1) Exterior outlets installed on a detached garage shall be GFCI protected as per 26-712(n) but are not required to be fed from a separate circuit.

2) The wires can be terminated in the panel but not installed onto the breakers or they can be just installed to the panel and not terminated – your choice.

3)
CAFCI protection for receptacles is not required for detached garages.