12 gauge wire is needed for 20A circuits. Table 3 in the CEC is misleading as in the table says 14 gauge is acceptable for 20A, however, the subrules it states that isn't. You can just use white electrical tape to properly identify it. It will work the same just show you put in the effort to properly identify it and I'm sure the inspector will pass it.