View Single Post
Old 04-23-2013, 07:11 AM   #8
Bindair Dundat
Scoring Winger
 
Join Date: Feb 2010
Location: St. Albert
Exp:
Default

Quote:
Originally Posted by ricosuave View Post
The receptacles you refer to, do they have UPSs installed on them, or on the same circuit as them?

I'm also wondering if it is a bad connection on the neutrals on those circuits, bad splice somewhere. Loose neutrals can cause strange things to happen.
That would be my guess as well. Likely as not, one of the connectors with a number of neutrals spliced together has failed and is breaking the connection back to the buss bar at the panel. Sharing neutral paths is permissible among light and plug circuits when this is the most practical way to wire these circuits. The condition you describe leads me to believe that this is the case here. Call in a sparky; this situation is potentially catastrophic. The bad connection is probably in a multigang switchbox; this is where I would look first.
Bindair Dundat is offline   Reply With Quote